I converted this to .JPG and then downsized it to meet the max res requirements, I'm not sure if it will be legible or not.
The way regulators work is they are trying to source current to maintain a particular voltage, typically in the 13.5-14.0V range for 12VDC systems. Depending upon the regulator design, it can be that the ripple of the regulator is a problem and the alternators fight each other (one source current into the other as the ripples are out of phase). Yamaha engines do not have this problem (I finally spoke to an engineer at the factory). Solution used to be running a phase synch signal between the alternators.
What you will get with two engines in parallel, is that both will source current to your electrical load if and only if the voltage is below the regulator set point on both engines. This will happen naturally if the electrical demands exceed that can be sourced by one engine. Note that the setpoint for both engine regulators is never going to be exactly the same. On my setup, I see the house load migrating quite dynamically across each engine (the voltmeters see what is happening at the engine, not at the house battery). I see voltage droops as a particular engine engages the load, and I see this migrate pretty nicely. I haven't gotten into a condition yet to require more than one alternator (i.e. greater than 35A), but if I do, both alternators will then be in action (at varying levels depending on the resistive differences inherent to each load).
Yes, Yamaha has the house feed, I like the following approach, very flexible, and I can maintain complete isololation with a starting battery in complete full reserve. There are many variations to this solution, this is what I chose, and so far works very well for me.
Hope this helps.
Cheers, HC